A 15A EVSE needs a 20A breaker, never higher than that, and not lower. Do not use a 30A or 40A or 50A breaker on a line feeding a 15A EVSE. The breaker is there to trip and turn off the juice should the EVSE malfunction and start drawing more current than it should. A 30A breaker for a 15A EVSE could allow a malfunctioning EVSE to overheat and potentially start on fire.
The wire size for the circuit can be heavier duty (future proofing) than needed for a 20A line, but the breaker must be right-sized to the device plugged in at the other end. The EVSE manufacturer's install manual will specify the breaker size needed for their device. Use that, not a larger amp breaker.
The wire size for the circuit can be heavier duty (future proofing) than needed for a 20A line, but the breaker must be right-sized to the device plugged in at the other end. The EVSE manufacturer's install manual will specify the breaker size needed for their device. Use that, not a larger amp breaker.