Discussion Starter · #1 ·
I have read that the charge cord for the volt should not be connected to an outlet via an extension cord...

Thoughts from the group?


Sent from my iPhone using Tapatalk
 

·
Registered
Joined
·
2,130 Posts
I have read that the charge cord for the volt should not be connected to an outlet via an extension cord...

Thoughts from the group?


Sent from my iPhone using Tapatalk
I'll never use one. Why would I?
Using it outside the home also creates a huge liability concern most of the time as well. I have a gasoline motor to get me where I need to be if a plug isn't available :)
 

·
Registered
Joined
·
1,381 Posts
Well, not all of us have garages, and if you have an outdoor plug with a rainproof cover, you almost have to use an extension cord due to the very short pigtail at the top of the EVSE.

IMHO, the reason they say that is so that Joe Public doesn't take a flimsy cord they have lying around and try to charge at 12amps. If you have a thick, quality cord plugged into a GFI outlet and protect the connections from the elements, I don't see how it's dangerous. My advice is to build your own cord, since the crimped connectors on store-bought ones are usually the weak link and will fail over time. Home Depot sells power cord by the foot, so you can make it only as long as needed (long cords waste energy and can trap heat if they're coiled up too much, I use 8'). Get weather-rated 12AWG cable and buy quality screw connectors. Check them for heat after construction and once a month thereafter. My EVSE lives in a rubbermaid container, so all connectors are protected from the weather.

I also have a quality 25' cord that I use when I visit friends/family far away (1-2x / year), but it will never pay for itself in gas savings. I almost regret buying it, but it is nice showing new people how it all works and getting a charge if we drive around town. If I'm on a road trip and staying at hotels, I don't even bother trying, it's not worth the hassle to save $2 on gas.
 

·
Registered
Joined
·
1,200 Posts
Short answer: No. it is generally not safe to do so.

Long answer: Depends. the Volt will be consistently drawing 8A to 12A over the 110V circuit. Even if you use an extension cord with a thick gauge (like 14 gauge for cords less than 25 feet, or 12 gauge for cords between 25 and 50 feet), there are many other factors -- such as the connection between the plug points (which is usually where oxides build up, and cause increased resistance), tripping hazard, risk of getting wet, etc .. which altogether determine if it is safe to use an extension cord.

So, can it be done? Yes .. but it carries a certain degree of risk, and may even be illegal where you live.
 

·
Registered
Joined
·
4,405 Posts
It is undoubtable safer not use an extension cord. For anything.
That being said, if you are going to it, use a quality cord, 12g or 10g, NOT 14 gauge. Shorter is better. Leave it at the 8 amp setting. Check for discoloration at both ends of cords, and discard if signs of heat damage appear.
We used to do it when all three Volts were here occasionally, but not anymore. One car left for college, and I also added a third L2 charger circuit.
 

·
Registered
Joined
·
1,624 Posts
I have read that the charge cord for the volt should not be connected to an outlet via an extension cord...
Thoughts from the group?
Sent from my iPhone using Tapatalk

FAQ re 120v charging
http://gm-volt.com/forum/showthread.php?48937-120V-Charging-FAQ

Article 625 of the National Electrical Code (NEC) limits the length of extension cords used with EVSE and permits their use only under certain circumstances. This paper from UL provides some additional info regarding the requirements in Article 625 of the NEC.
http://www.ul.com/global/documents/...sletters/electricalconnections/November10.pdf

The most recent version of Article 625 I found online is from 2008.
http://www.calstart.org/Libraries/E...ents/Article_625_Natl_Electric_Code.sflb.ashx
The most recent version was published in the last year or two and includes lots of changes. I was able to read a copy in the reference section of my library.

KNS

EDIT: Info about the most recent version of Article 625 can be found here
http://ecmweb.com/nec/article-625-electric-vehicle-charging-systems
Free registration is required. I didn't bother.
 

·
Registered
Joined
·
1,888 Posts
I use an extension cord, but only occasionally. I have found that most of the molded plugs on the ends of ready-made cords are not very good, and will tend to heat up. My 12-2 w/g cord doesn't get warm, but the plug did. So I cut it off and replaced it with a much better plug from Home Depot. Problem solved. So far, the female end of the cord is OK, but I'll probably replace it as well just to be sure.
 

·
Registered
Joined
·
81 Posts
I've also used a 50ft. 10g heavy duty extension cord since 2012, no problem. I think the reason no one would ok it is that some people might use a light duty cord or I should say mis-use it.
 

·
Registered
Joined
·
3,811 Posts
.... My 12-2 w/g cord doesn't get warm, but the plug did. So I cut it off and replaced it with a much better plug from Home Depot. Problem solved. ...
The Volt EVSE would require a 12 gauge - 3 wire cord to work.
I have used an 12-3 cord longer than 25 ft from day one.
12 gauge in the wall. 12 gauge in the cord. What's the difference as long as all the connections are in good conditions?
 

·
Registered
Joined
·
1,539 Posts
I can't speak for US driver's handbook but the Ampera handbook says you can use an extension lead with the 6A charging rate option. (at 230V).

I've done this a couple of times, and all the plug connects remain completely cold to the touch at that current rating.
 

·
Registered
Joined
·
5,431 Posts
As an EE, I agree with many of the posts here. If your extension need is occasional, get the best 10 gage, 20 A extension you can buy. Invest more and be safe. Keep all plug contacts on both the EVSE and extension polished and clean. All extra connections add resistance points to the electrical path, and each point generates heat and becomes a power loss.

But if you do need an extra long cable with your EVSE all the time, it is safer to replace the original NEMA cord and plug with a longer and heavier cable, and a 15 A or more plug. The cable replacement is a DIY job, but if you don't have the skills or tools, ask a good electrician to do it. Pay up more and get a sale, long lasting extension.
 

·
Registered
Joined
·
1,888 Posts
The Volt EVSE would require a 12 gauge - 3 wire cord to work.
I have used an 12-3 cord longer than 25 ft from day one.
12 gauge in the wall. 12 gauge in the cord. What's the difference as long as all the connections are in good conditions?
12-2 w/g is three wire cord; a black, a white, and a green ground wire.
 

·
Registered
Joined
·
3,544 Posts
When necessary, I use a 10 gauge extension cord at work and have never had a problem.
 

·
Registered
Joined
·
874 Posts
I've charged my Volt on a 25' 12 gauge extension cord every night and it's been completely fine. The only outlet in my garage near where my car goes is on the ceiling, so I need an extension cord for the EVSE to be able to be plugged in. The plug gets slightly warm, but not even nearly as warm as a phone charger does while charging, so I'm not worried.

If you need to use an extension cord, don't go over 25 feet 12 gauge or 50 feet 10 gauge and be sure it's a high quality cord that is kept out of the elements when not in use.
 

·
Registered
Joined
·
2,130 Posts
The Volt EVSE would require a 12 gauge - 3 wire cord to work.
I have used an 12-3 cord longer than 25 ft from day one.
12 gauge in the wall. 12 gauge in the cord. What's the difference as long as all the connections are in good conditions?
Basically a true statement; however, you get into distance. With an extension cord you might be well over any distance that a house may have. This is where a 10 gauge cord would be best. Basically if you are under 50 feet a 12 gauge cord is fine. Over that a 10 gauge cord is fine. GM is simply limiting its liability so a person doesn't use a 16 or 14 gauge extension cord and start a fire.
 

·
Registered
Joined
·
716 Posts
I've been charging nightly at 12 amps through a 12-foot appliance extension cord for 6 years. My nearest socket is on the garage ceiling, so I needed the extension. It is a supposed heavy-duty cord.

A key reason, rarely cited, that GM discourages use of an extension cord is that the charger's 120V plug has an over-temp sensor that will stop the charging process if the plug or socket gets too hot. That sensor is unable to sense heat at the extension cord's plug end, so suddenly there is an un-monitored plug-and-socket where potentially a fire could start. I occasionally check the temperature at that junction while charging just to make sure it's still staying cool. Never had a problem there.
 

·
Registered
Joined
·
591 Posts
Been using a 25 foot 12ga extension cord purchased from Lowes for 5 years occasionally on the Volt, frequently on my 12 ton log splitter. No issues.
 

·
Registered
Joined
·
1,234 Posts
Use 2 10 gauge 3 wire outdoor extensions to charge our volts. All connections are secured, locked up and out of the elements (with the evses in a locked shed near our driveway). No heat and no issues, even at 240 v.


Sent from my iPhone using Tapatalk
 

·
Registered
Joined
·
97 Posts
The theoretical reason you are not supposed to is that there is a limit to the allowable distance between the outlet and the GFCI circuitry. If you use an extension cord, that distance is exceeded. This distance is the reason for the very short cord. So you are not supposed to use one.

That said, so long as you use a properly rated extension cord, of course it will work. The electricity came from the power plant, wherever it may be, crossed deserts and mountains or whatever, ran around your city, and through your walls. Do you think it cares if it goes another 25 feet or whatever through an extension cord?
 